katwalatapan
Electrical
- Aug 9, 2011
- 153
Hello,
I have a query concerning multiple ATS configuration for single, SG050, 50kW, 3-phase, 120/208V, generator.
I'm considering a scenario, where a 200A, 3-Pole, HTS series ATS is connected to the SG050 generator. The 200A, ATS feeds a 200A, 3-phase, 120/208V, emergency panel. Nine (9), 50A, 2-Pole, RTG series ATS with load center would be installed in the apartment units, which would be connected to the emergency panel during a power outage. As per the product spec sheets the utility sensing and load transfer could be configured from the SG050 generator controller and the 200A, HTS series ATS. The RTG series uses utility sensing and timing functions from the generator as per the spec sheet. Based on the above scenario, I have the following queries:
1. With both the SG050 and the HTS series ATS providing utility sensing and load transfer, should the generator or the ATS be configured for voltage sensing and transfer?
2. Is control wiring required from the Nine (9), 50A, RTG series ATSs to the generator for operation i.e. transfer load from utility to generator and vice versa? If so, then would we have to home run the control wiring from the ATSs to the generator OR could we combine the control wiring from all the nine (9), ATSs and send one (1) control wire to the generator for transfering load from utility to generator and vice-versa?
I'd appreciate your assistance on this matter.
Thank you.
I have a query concerning multiple ATS configuration for single, SG050, 50kW, 3-phase, 120/208V, generator.
I'm considering a scenario, where a 200A, 3-Pole, HTS series ATS is connected to the SG050 generator. The 200A, ATS feeds a 200A, 3-phase, 120/208V, emergency panel. Nine (9), 50A, 2-Pole, RTG series ATS with load center would be installed in the apartment units, which would be connected to the emergency panel during a power outage. As per the product spec sheets the utility sensing and load transfer could be configured from the SG050 generator controller and the 200A, HTS series ATS. The RTG series uses utility sensing and timing functions from the generator as per the spec sheet. Based on the above scenario, I have the following queries:
1. With both the SG050 and the HTS series ATS providing utility sensing and load transfer, should the generator or the ATS be configured for voltage sensing and transfer?
2. Is control wiring required from the Nine (9), 50A, RTG series ATSs to the generator for operation i.e. transfer load from utility to generator and vice versa? If so, then would we have to home run the control wiring from the ATSs to the generator OR could we combine the control wiring from all the nine (9), ATSs and send one (1) control wire to the generator for transfering load from utility to generator and vice-versa?
I'd appreciate your assistance on this matter.
Thank you.