Multiple Battery Charger Demand

Status
Not open for further replies.

WoodrowJWeen

Electrical
Jul 30, 2003
112
Anyone know what sort of demand factor could be applied to the AC input load of multiple battery chargers for golf carts? This involves over 50 carts. I'm assuming the chargers are integral with the carts but not being a golfer I don't know if this is true. Not that it would matter.
 
Replies continue below

Recommended for you

At the end of a busy day, all the carts may be returned to the charging area and all put on charge simultaneously.
The demand factor will be 100% UNLESS you have specific information otherwise.
Bear in mind the consequences of a "loss of revenue event" due to not enough carts being ready when needed due to an inappropriate demand factor.
respectfully
 