coldkeeper1
Mechanical
- Apr 26, 2008
- 12
This marine chiller seems to be a custom made unit. It uses a variable capacity screw-type compressor coupled to three identical shell-and-tube evaporators. The water outlet pipe of each evaporator runs independently, before being combined into a single main outlet pipe. Simply stated, the problem is that chilled water is not coming out cool enough: 49F versus the required 44F, with compressor at full capacity.
I´ve noticed that the water outlet temperature at each evaporator is not the same (44F, 46F, 52F). They all have been internally cleaned recently. Pressure drop and water flow is about the same for each evaporator, so heat load can be assumed more or less evenly distributed
Each evaporator is feeded by an independent TXV, all of them of the same tonnage, all of them connected to a main liquid line, and all of them located in an absurdly hard to reach location.
Before getting into the nightmarish job of removing the TXV´s, I would like to ask for your opinion: is it possible, in such a parallel feeding arrangement, that the majority of the liquid refrigerant might be choosing to follow the path of less resistance (let´s say, across the two txv´s feeding the 44F and 46F water outlet evaporators) while mostly ignoring the 52F circuit maybe due to a partially closed TXV?
I´ve noticed that the water outlet temperature at each evaporator is not the same (44F, 46F, 52F). They all have been internally cleaned recently. Pressure drop and water flow is about the same for each evaporator, so heat load can be assumed more or less evenly distributed
Each evaporator is feeded by an independent TXV, all of them of the same tonnage, all of them connected to a main liquid line, and all of them located in an absurdly hard to reach location.
Before getting into the nightmarish job of removing the TXV´s, I would like to ask for your opinion: is it possible, in such a parallel feeding arrangement, that the majority of the liquid refrigerant might be choosing to follow the path of less resistance (let´s say, across the two txv´s feeding the 44F and 46F water outlet evaporators) while mostly ignoring the 52F circuit maybe due to a partially closed TXV?