bmlxd40
Mechanical
- Oct 7, 2011
- 82
I have a highrise building with the two FDC’s as specified in NFPA 14, 2013 ed., chapter 7.12.2. The FDC’s are two inlets each. This is in compliance with 7.12.3.3, even though the total standpipe demand is 750 GPM.
In some situations with a greater standpipe demand, we may have one FDC with a 6” piping connection & more than two inlets. We would still have the remotely located FDC with a 4” connection and two inlets.
My questions is:
When calculating to the FDC to obtain the required pressure at the FDC, should the demand be split with 500 GPM flowing through the most remote (Or smaller) FDC, and the other 250 through the closer (Or larger) FDC?
In some situations with a greater standpipe demand, we may have one FDC with a 6” piping connection & more than two inlets. We would still have the remotely located FDC with a 4” connection and two inlets.
My questions is:
When calculating to the FDC to obtain the required pressure at the FDC, should the demand be split with 500 GPM flowing through the most remote (Or smaller) FDC, and the other 250 through the closer (Or larger) FDC?