bentov
Electrical
- Feb 2, 2004
- 74
A customer has a 60hp pump supplied by a remote (300ft away) 480/277V service, so the neutral conductor is not present at the pump (ground only). 125ft from that is a 600a 240/120V 3ph 4W delta service supplying (2) greenhouses on separate 200a branch feeder breakers. Next to that service they've parked a new 150kw 480/277 4 lead generator - pump company plans to pull power from there to the 60hp pump, locating a manual transfer switch over at the pump panel. My job is to use the same generator to supply the greenhouses (total load for both around 100a, looks like).
So I see how to add a 45kva delta delta (or wye delta) transformer with primary and secondary protection to the genset. I'll need to use (2) 200a manual transfer switches for the greenhouses(cause have to pull from the load side of the existing feeder breakers, can't access the line sides supported by the buss standoff hardware, likewise can't access the losd side of the main switch - all bolted together).
So right next to each other I'll have the 600a 240/120 service mid tapped neutral, the 250a 480/277 generator neutral (with factory jumper to genset frame ground), and my new transformer mid tapped neutral. I guess there's also a 4th neutral, back at the 200a service for the pump, though no conductor is present. I should just tie all those neutrals together, right, then bond them to the service entrance earth rod? Been reading threads, and the code, not really finding a similar situation . . .
So I see how to add a 45kva delta delta (or wye delta) transformer with primary and secondary protection to the genset. I'll need to use (2) 200a manual transfer switches for the greenhouses(cause have to pull from the load side of the existing feeder breakers, can't access the line sides supported by the buss standoff hardware, likewise can't access the losd side of the main switch - all bolted together).
So right next to each other I'll have the 600a 240/120 service mid tapped neutral, the 250a 480/277 generator neutral (with factory jumper to genset frame ground), and my new transformer mid tapped neutral. I guess there's also a 4th neutral, back at the 200a service for the pump, though no conductor is present. I should just tie all those neutrals together, right, then bond them to the service entrance earth rod? Been reading threads, and the code, not really finding a similar situation . . .