cornemo
Mechanical
- Apr 23, 2009
- 55
I'm currently in a discussion with a terminal owner who has been told that the (flow) calculations for the fire fighting and foam systems have to be done by the manufacturer/supplier(like Tyco). He says that calculations made by an independent engineering company are not valid unless they are approved by the manufacturer/supplier of the system.
I can't find any reference in NFPA for the above statement. If I check for example NFPA 11, chapter 4, 4-4.2 for example it says that "Complete plans.......shall be submitted by the engineer or contractor...." Which in my opinion allows an independent engineering company to do the calculations.
Is there any reference in one of the many NFPA codes which adresses the issue of who can/must make the calculations for the system? Or does someone have experience with this issue?
Thanks in advance for your replies.
With regards, Corné
I can't find any reference in NFPA for the above statement. If I check for example NFPA 11, chapter 4, 4-4.2 for example it says that "Complete plans.......shall be submitted by the engineer or contractor...." Which in my opinion allows an independent engineering company to do the calculations.
Is there any reference in one of the many NFPA codes which adresses the issue of who can/must make the calculations for the system? Or does someone have experience with this issue?
Thanks in advance for your replies.
With regards, Corné