dtour
Electrical
- Jun 28, 2017
- 2
I was hoping to get some in input on potential root causes for the activation of an 86 lock-out relay specifically used for a breaker failure feature (referred to as 86BF on the attached drawings). We took down a large portion of our facility due to the activation of this 86BF that I found to be tripped with no trip command sent from the protection relay. There was no fault, or equipment damage found. Equipment was energized again with no issues; 86BF reset just fine.
This has actually happened before on this same switchgear/breaker line-up but not on the 86BF, rather just the 86 lock-out relay that trips the local medium voltage breaker; breaker was tripped, 86 was found tripped but the protection relay did not issue a trip command.
The circuit seems pretty simple, so I'm not really sure how that 86BF lock-out relay coil could have been energized. It sits on a 125VDC system, that typically operates 130-133VDC. The indicator light is a full voltage (direct connected) LED, that was found to be working just fine after the event.
Thanks in advance.