JuanBC
Electrical
- Nov 28, 2017
- 141
Hello,
I would like your guidance calculating the required kVA a source should have to test a MV cable doing an AC Hipot test.
The test described in IEC 60502-2 consist on applying phase-to-phase voltage for 15 minutes at a frecuency of 20 to 300 Hz between the conductor and the metal screen/sheath.
We are willing to test the following cable: 2 AWG 3/C CU 15KV 220 NL-EPR 133% TS ARMOR-X PVC MV-105
Based on datasheet (attached) the reactance Xc@60Hz is 0.053 Mohm/Mft. Is this reactance value between conductors? Or is from one conductor to ground (screen)?
If I am not wrong, the required power should be kVA.required = U^2/Xc = U^2/(1/wC) where U should be test voltage, 15 kV and C the capacitance from one conductor to ground, in F
Thank you in advance
JBC
.......
"The more I read, the more I acquire, the more certain I am that I know nothing"
I would like your guidance calculating the required kVA a source should have to test a MV cable doing an AC Hipot test.
The test described in IEC 60502-2 consist on applying phase-to-phase voltage for 15 minutes at a frecuency of 20 to 300 Hz between the conductor and the metal screen/sheath.
We are willing to test the following cable: 2 AWG 3/C CU 15KV 220 NL-EPR 133% TS ARMOR-X PVC MV-105
Based on datasheet (attached) the reactance Xc@60Hz is 0.053 Mohm/Mft. Is this reactance value between conductors? Or is from one conductor to ground (screen)?
If I am not wrong, the required power should be kVA.required = U^2/Xc = U^2/(1/wC) where U should be test voltage, 15 kV and C the capacitance from one conductor to ground, in F
Thank you in advance
JBC
.......
"The more I read, the more I acquire, the more certain I am that I know nothing"