Hi,
I've had a search through the forum but can't find something specifically applicable to my query.
I normally work in the design of LV works, but in this instance am involved in the design and build of a handful of 11/0.415kV distribution substations connected to an existing industrial plant.
My work is being overseen and signed off by a registered engineer but I'm trying to undertake my own learnings at the same time.
With regards to the cable design and short-circuit withstand, on LV works, this is purely determined in relation to the clearing time of the upstream protective device and the earth conductor the same.
However with regards to MV, I understand in some circumstances, such as tolerable step & touch potentials, the back-up protection is considered rather than the immediate upstream protective device. Is this also the case with short-circuit withstand of a cable, should I consider up-stream or back-up protection clearing time?
Further, with the cable screen, since, with respect to short-circuit withstand, is only in relation to an earth fault, is it considered that the withstand is only considered with respect to part of the earth fault short-circuit current, given that a part of the current returns via the earth?
I had read some literature that indicated the screen needed to withstand the full E.F. short-circuit current for the case of insulation failure, where the arc pressure will likely rupture the cable and result in a two or three phase to earth fault.
Thanks
I've had a search through the forum but can't find something specifically applicable to my query.
I normally work in the design of LV works, but in this instance am involved in the design and build of a handful of 11/0.415kV distribution substations connected to an existing industrial plant.
My work is being overseen and signed off by a registered engineer but I'm trying to undertake my own learnings at the same time.
With regards to the cable design and short-circuit withstand, on LV works, this is purely determined in relation to the clearing time of the upstream protective device and the earth conductor the same.
However with regards to MV, I understand in some circumstances, such as tolerable step & touch potentials, the back-up protection is considered rather than the immediate upstream protective device. Is this also the case with short-circuit withstand of a cable, should I consider up-stream or back-up protection clearing time?
Further, with the cable screen, since, with respect to short-circuit withstand, is only in relation to an earth fault, is it considered that the withstand is only considered with respect to part of the earth fault short-circuit current, given that a part of the current returns via the earth?
I had read some literature that indicated the screen needed to withstand the full E.F. short-circuit current for the case of insulation failure, where the arc pressure will likely rupture the cable and result in a two or three phase to earth fault.
Thanks