AusLee
Electrical
- Sep 22, 2004
- 259
Hello,
I have an installation running for more than 5 years. No new loads have been added, still the same from day 1 in service.
For some reason, the local civil engineer claims that the transformer is heating. A site investigation reveals air no hotter than leaving a normal house hold winter time radiator. The 1,250 kVA dry type transformer is "Class F", it is allowed to overheat 100 degrees above ambient temperature.
The transformer is equipped with a thermal protection relay, and last year the MV breaker was changed (just because the civil engineer deemed it had operated enough).
Now, for some reason, the new MV circuit breaker is tripping occasionally, once every 2-3 days. The load on the transformer is about 700A, less than 40% (it is a well oversized transformer). The civil engineer wants to change the transformer as well.
I have checked the MV voltage on site, it is near exact match with the tap setting, no over or undervoltage. Since the load is still the same, i assume either the new MV breaker is faluty, or is set to trip at way below the rated current, or the thermal relay is faulting and causing the breaker to trip.
Can you please advise on what may be the reason of these nuisance trippings, and what tests can be made on site to point the real reason for the tripping?
I have an installation running for more than 5 years. No new loads have been added, still the same from day 1 in service.
For some reason, the local civil engineer claims that the transformer is heating. A site investigation reveals air no hotter than leaving a normal house hold winter time radiator. The 1,250 kVA dry type transformer is "Class F", it is allowed to overheat 100 degrees above ambient temperature.
The transformer is equipped with a thermal protection relay, and last year the MV breaker was changed (just because the civil engineer deemed it had operated enough).
Now, for some reason, the new MV circuit breaker is tripping occasionally, once every 2-3 days. The load on the transformer is about 700A, less than 40% (it is a well oversized transformer). The civil engineer wants to change the transformer as well.
I have checked the MV voltage on site, it is near exact match with the tap setting, no over or undervoltage. Since the load is still the same, i assume either the new MV breaker is faluty, or is set to trip at way below the rated current, or the thermal relay is faulting and causing the breaker to trip.
Can you please advise on what may be the reason of these nuisance trippings, and what tests can be made on site to point the real reason for the tripping?