any guru,
I am facing the problem that
MV (6.6 kV) motor (1250 kVA) of compressor broken but VCB didn't trip.
The VCB was opened by operator when they hear big noise and vibration.
our Setting is
Motor start time = 9 s
Lock rotor relay;
= 300% In
t= 9s
50 Relay;
I=8.5 In
t=15 ms
49 TOL;
I=250
t=1.3 s
Unbalance relay
How about setting of 51LR lock rotor relay (REF 542+)?
Is it too lond time for 9s?
What is normal practic for 51LR setting?
Why VCB didn't trip before motor damaged ?
Thanks for your answer
young eng.