Can anyone give me some guidance or point me to some technical papers regarding the use of medium voltage breakers vs starters based on starts/stops a day?
All of my company's power plants were built in the 1950s and 1960s and were originally baseload. All 4kV motors were supplied from switchgear breakers and for the most part were started when the unit was brought on and stopped when the unit came off. In the past few years, due to deregulation and the competitive market, we have been forced to cycle our units to follow load and as a result see more starts/stops on our 4kV motors. For instance, for our pulverized coal units, mills might typically get started stopped twice a day with load changes.
Recently we had a breaker failure lead to a switchgear fire. Approximately 30 minutes after one of our more frequently cycled motors was started (by closing breaker) there was a bus overload trip and operators found a switchgear fire. The fire originated from the aforementioned breaker cubicle. The breaker was just about completely destroyed, so visually there was nothing of value that could be gained from inspecting it postmortem. Based on this sequence, our assumption is that the breaker main contacts made up poorly due to eroded surfaces or poor alignment and heated up and started on fire. The breaker had been rebuilt within the past two years by a qualified shop, so lack of maintenance is not believed to have been an issue.
I am trying to put together recommendations as a follow up to this event. I believe that several manufacturers can offer motor starter retrofits into original switchgear lineups. Is such a retrofit worthwhile if we are talking about two starts/stops per day? Also, under the assumption that contact wear due to number of operations was a contributor and if two starts/stops a day is not excessive, would switching to a vacuum retrofit breaker make sense as a recommendation? My assumption being that contact wear is less of a problem in vacuum breakers vs air breakers.
Thanks.
All of my company's power plants were built in the 1950s and 1960s and were originally baseload. All 4kV motors were supplied from switchgear breakers and for the most part were started when the unit was brought on and stopped when the unit came off. In the past few years, due to deregulation and the competitive market, we have been forced to cycle our units to follow load and as a result see more starts/stops on our 4kV motors. For instance, for our pulverized coal units, mills might typically get started stopped twice a day with load changes.
Recently we had a breaker failure lead to a switchgear fire. Approximately 30 minutes after one of our more frequently cycled motors was started (by closing breaker) there was a bus overload trip and operators found a switchgear fire. The fire originated from the aforementioned breaker cubicle. The breaker was just about completely destroyed, so visually there was nothing of value that could be gained from inspecting it postmortem. Based on this sequence, our assumption is that the breaker main contacts made up poorly due to eroded surfaces or poor alignment and heated up and started on fire. The breaker had been rebuilt within the past two years by a qualified shop, so lack of maintenance is not believed to have been an issue.
I am trying to put together recommendations as a follow up to this event. I believe that several manufacturers can offer motor starter retrofits into original switchgear lineups. Is such a retrofit worthwhile if we are talking about two starts/stops per day? Also, under the assumption that contact wear due to number of operations was a contributor and if two starts/stops a day is not excessive, would switching to a vacuum retrofit breaker make sense as a recommendation? My assumption being that contact wear is less of a problem in vacuum breakers vs air breakers.