MV Switch Testing 1

Status
Not open for further replies.

EEJaime

Electrical
Jan 14, 2004
536
We have been asked to complete a project designed by someone no longer involved on a project. One item they called for was the addition of a section to an existing switchboard lineup. Adding one section containing a fusible switch. It is a 400A, 4.16kV, 3P switch. There is no testing specification. What would be the minimum recommended tests that we should require of the installing contractor? We can refer to a NETA test procedure, but what do you gents feel are the important tests both pre-installation and when the busses are connected and the section is installed and ready to be energized?
 
Replies continue below

Recommended for you

The NETA procedure ia what you should follow. (ATS, not MTS)
 
As a minimum, beyond the mechanical tests as recommended by the mfgr such as slow close and alignment, etc a megger test of the insulation and contact resistance test would be prudent.
Optionally, the insulation system can be DC high potential tested.
JIM

 