Hi, I have a question regarding switchgear hopefully some one can assist please.
We have a project to install a 3-way switch RMU (ring main unit) in an installation with the following power system details:
11kV, 200A maximum load, protection trip setting 200mS, Fault Levels: Ik"=21.7kA 3ph, Ib=13.6kA 3ph, Ip=41.8kA 3ph.
We are looking at the ABB Safelink RMU as a cost effective solution and the specifications given for this unit are:
12kV, 630A Rated Current, Withstand Current 20kArms/3sec, Internal Arc Fault Withstand 20kA, Load Break Switch Short Circuit Making Current 50kA peak.
I am unsure whether the ABB unit meets all the system fault level criteria, in particular the 20kA rating of the ABB unit is less than the 21.7kA system fault level. The I2t of the ABB unit (20kA/3sec) will be greater than the system I2t (21.7kA/0.2s). So does this mean the ABB unit meets the installation power system requirements based on the I2t or other considerations needed.
I use the I2t criteria for cable fault rating, however I'm not sure whether it can be applied to switchgear. I normally specify MV switchgear with kA rating higher than the system fault level, however in this installation the ABB unit is a very cost effective solution for us so I would appreciate any feedback on this issue.
Thanks.
We have a project to install a 3-way switch RMU (ring main unit) in an installation with the following power system details:
11kV, 200A maximum load, protection trip setting 200mS, Fault Levels: Ik"=21.7kA 3ph, Ib=13.6kA 3ph, Ip=41.8kA 3ph.
We are looking at the ABB Safelink RMU as a cost effective solution and the specifications given for this unit are:
12kV, 630A Rated Current, Withstand Current 20kArms/3sec, Internal Arc Fault Withstand 20kA, Load Break Switch Short Circuit Making Current 50kA peak.
I am unsure whether the ABB unit meets all the system fault level criteria, in particular the 20kA rating of the ABB unit is less than the 21.7kA system fault level. The I2t of the ABB unit (20kA/3sec) will be greater than the system I2t (21.7kA/0.2s). So does this mean the ABB unit meets the installation power system requirements based on the I2t or other considerations needed.
I use the I2t criteria for cable fault rating, however I'm not sure whether it can be applied to switchgear. I normally specify MV switchgear with kA rating higher than the system fault level, however in this installation the ABB unit is a very cost effective solution for us so I would appreciate any feedback on this issue.
Thanks.