umrpwr
Electrical
- Dec 21, 2002
- 71
I would appreciate others feedback on the following situation.
A customer of mine has one phase cable in a 5kV duct bank approximately 600' in length with parallel runs that has gone bad and needs to be replaced. The cable is 2250 kCmil Al and approximately 40 years old. Due to age of the cables in the duct back and the fact that that particular size of cable is not readily available the customers engineer has requested that we repair the cable by splicing a smaller cable onto the undamaged cable portion of the cable in the run at a manhole. The new cable would be 2000kCmil and would be approximately 100' in length of the total 600'. The feeder is lightly loaded and not loaded near capacity.
I have recommended against repairing the cable in such a manner and am concerned about what other liabilities and problems may result. Besides being generally bad engineering and construction practices my arguments against do the repair are the following:
Ideally the ownwer would replace all of the cables in the duct at the same time due to the age of the cables. The reasons I told the owner against doing such a repair are:
1.) The age of the other existing cables and remaining life
2.) The new phase cable will have a different impedance and be unbalanced. This problem will become prevalent at heavier loading.
The owner being cost conscious uses the following justification and reasoning for their argument.
1.)The other cables may not be able to be replaced easily in the existing duct bank because of the age.
2.)The feeder is only lightly loaded and any imbalance between phases and cables will not be significant enough to matter.
As a compromise between two the one other option would be to splice new cables of equal length onto all of the phase cables from the manhole. However this is less than ideal and adds another potential point of failure.
I would appreciate any comments on the above situation.
A customer of mine has one phase cable in a 5kV duct bank approximately 600' in length with parallel runs that has gone bad and needs to be replaced. The cable is 2250 kCmil Al and approximately 40 years old. Due to age of the cables in the duct back and the fact that that particular size of cable is not readily available the customers engineer has requested that we repair the cable by splicing a smaller cable onto the undamaged cable portion of the cable in the run at a manhole. The new cable would be 2000kCmil and would be approximately 100' in length of the total 600'. The feeder is lightly loaded and not loaded near capacity.
I have recommended against repairing the cable in such a manner and am concerned about what other liabilities and problems may result. Besides being generally bad engineering and construction practices my arguments against do the repair are the following:
Ideally the ownwer would replace all of the cables in the duct at the same time due to the age of the cables. The reasons I told the owner against doing such a repair are:
1.) The age of the other existing cables and remaining life
2.) The new phase cable will have a different impedance and be unbalanced. This problem will become prevalent at heavier loading.
The owner being cost conscious uses the following justification and reasoning for their argument.
1.)The other cables may not be able to be replaced easily in the existing duct bank because of the age.
2.)The feeder is only lightly loaded and any imbalance between phases and cables will not be significant enough to matter.
As a compromise between two the one other option would be to splice new cables of equal length onto all of the phase cables from the manhole. However this is less than ideal and adds another potential point of failure.
I would appreciate any comments on the above situation.