MVA, MVAR & MW ?? 3
shadmani
Controls guy here, trying to understand the hardcore power stuff. I recently visited a power plant and was kind a surprised the way the power is dispatached. Not only they were trying to maintain a certain MW load output from the station, from time to time, they were also somehow adjusting the MVAR on the machine (operators did not knew how exactly how MVAR is manipulated, they did tell me it is required based on the load on the grid and is requested to be adjusted by the dispatcher).
Could someone please, in simple terms, explain the relationship between MW, MVAR and MVA, why we talk all terms in power dispatch and what/why do we adjust the MVAR.
Thanks a bunch
MVA is the aparant power, MW is the real power and, MVAR is reactive power. If you remember your Circuit II course MVA is the Square Root of MW^2+MVAR^2. Just like a right triangle. It is actually called the power triangle. You adjust the MW of a plant based on the load on the grid. Generation = Load at all times. You adjust the MVAR of the machine to adjust grid voltage in the local area. MVARs are the result of the magnetic coupling needed to produce work with a machine. They are not exportable therefor you either have local generation or capacitor banks provide them. You adjust the MW of the machine with the amount of torque you apply to the input shaft of the machine. This usually means more steam to the turbine. This tries to speed up the machine against the grid and produces more power. You adjust the MVAR output of the machine by adjusting the exciter of the machine. That is to raise MVAR output you excite the machine more by increasing the current in the field (rotor). This increases the magnetic coupling of the rotor to the stator and increases the MVAR output.
BEPC13 explained it correctly however, it may be clearer to simply state that an MVAR meter in a power plant is a center zero device. By raising the machine volts the generator will export VARs to the system and conversely by decreasing the machine volts VARs will be imported to the generator. When I was working as a power plant operator shortly after graduating in the early 60s. Each power station on the grid had to maintain its voltage within given parameters. This generally mean't that the voltage on the outgoing line was had to be kept at its nominal kV. The power plant I operated, was on the end of a 132kV spur line some 120 miles from the main 330kV interconnected system, and the voltage used to vary substantially over 24hrs. During the night on light system loads, the voltage would rise and we would have to import VARs by lowering the generator volts and during peak periods on high system loads, raise the generator volts and export VARs to maintain nominal voltage on the 132kV feeder. I guess these days the system controllers spread the VAR loads around much better than we did in the old days.....
This is an interesting thread in light of a couple of recent threads on reactive power. They did not deal with what actually happened at the power station, however.
Now, I have a purely theoretical question. Since power factor is a function of load, reactive load, and VARS is a function of the PF, (if that is not right correct me right away) in a hypothetical system, a power plant supplies power to a grid that has lots of installed horse power, electric motors, creating a significant lagging power factor, and hence a given amount of VARS.
What happens when all those workers turn off their motor driven machines at the end of the work day and go home and turn on their electric space heaters, coffee pots, toasters, ovens, and lights. You get the picture, purely resistive load, approaching unity power factor.
Is something done at the power plant to correct, effect or change either of those conditions?
And, since the power companies are beginning to bill for the effects of reactive power, isn't it in the Utilities interest to not correct the PF?
rmw
PS: As I stated in one of the other threads, I am trying to comprehend this as an ME. I can make those turbines produce the torque, but I struggle to understand what you EE's do with it to ship it.
With regards to
"What happens when all those workers turn off their motor driven machines at the end of the work day and go home and turn on their electric space heaters, coffee pots, toasters, ovens, and lights. You get the picture, purely resistive load, approaching unity power factor" as aked by the previous thread, the following happens.
First of all as the overall system MW decrease, the system voltage tends to rise. To control the volts, inductive MVARs have to be generated by either switching in reactors or reducing MVARs by reducing volts on the generators supplying MVARs to the system.
With regards to Utility companies charging for MVARs. as it wattless current (except for I2R losses)utility companies do not have fuel costs generating VARs. So should only charge for generator losses etc. which would be very small.
The problem with var (yes; var, not VAR or VAr) is that it occupies transformers and transmission lines. Utilities therefore charge to keep var consumption low. If they were to deliver lots of Mvars, there would not be much rom for the MWs.
Gunnar Englund
Reactive power also happens to be the most misunderstood concept in the electric utility industry. This is mostly because it is usually described as the imaginary part of the load; therefore, people tend to believe that it does not exist or serves not useful purpose. Noting could be further from the truth.
Reactive power supply is essential for reliably operating the electric transmission system. “Inadequate reactive power has led to voltage collapses and has been a major cause of several recent major power outages worldwide”
One source for “supply” or “absolve” reactive power is a generator. For instance, when a generator is operating at certain limits, a generator can increase its dynamic reactive power is produced from equipment that can quickly change the Mvar level independent of the voltage level. Thus, the equipment can increase its reactive power production level when voltage drops and prevent a voltage collapse.
[blue]By convention, reactive power, like real power, is positive when it is “supplied” and negative when it is “consumed.” Consuming reactive power lowers voltage magnitudes, while supplying reactive power increases voltage magnitudes.[/blue]
We should keep in mind that a production or consumption of reactive power by a generator only could be done by reducing its production of real power. As a result, producing additional reactive power results in reduced revenues associated with reduced real-power production. This may be seen in the generator capability curve similar to the one enclose below.
The problem with var (yes; var, not VAR or VAr)...
Nitpick: The unit of Volt-Amp-Reactive is derived from the base units of Volts and Amps, both of which are named after actual people, so SI states that they should be capitalized when abbreviated, whereas 'reactive' is not based on a proper name and should not be capitalized.
Therefore, it should be formally abbreviated to VAr, but VAR (and flavours like kVAR and MVAR) seem to be the industry norms.
The unit of Volt-Amp-Reactive is derived from the base units of Volts and Amps, both of which are named after actual people, so SI states that they should be capitalized when abbreviated...
Nitpick^2: When VAR is used to stand for Volt-Amp-Reactive is that not an acronym rather than an abbreviation? If so, what does SI state re capitalization?
Reactive power must be produced by the utility to compensate for reactive power consumed in its own systems and for that consumed by customers. It utilizes T&D capacity and it wastes real power due to the I^2R losses it creates.
Generators, capacitors, synchronous condensers and static VAR compensators are all used to produce reactive power. Capacitors are usually distributed around the network for voltage control and to get VAR production as close to the VAR consumption as possible to minimize I^2R losses and capacity utilization. Switched capacitors are used to help stabilize voltage as reactive loads fluctuate.
Nitpick or not. The var (yes, var) is an SI unit on its own and shall be written var. Just like that.
It is not considered to be named after a human being and therefore it isn't spelled with capital letters. That used to be. But isn't any more.
Gunnar Englund
rmw... still travelling through south america?
regarding your question... in that part of the world several things happen...
1. in Uruguay there are power plants that have the generator working as a "synchronous condenser" i.e. the prime mover (usually a GT) is shutdown and the generator kept synchronized to the grid to absorb var (negative var)
Uruguay has very little industry... and because of the use of fluorescent light the reactive power is very high... therefore they use the synch cond. to improve the power factor (i.e. increase - absorb - var)
2. in Argentina, Chile, Uruguay the grid is not exactly stable... there are noticeable variations in the frequency during the day. usually the frequency falls below 50Hz
So... at night when the load is the lowest the grid dispatcher requests the operators to raise the load (no isochronous driver) so the frequency increases... to compensate for the low frequency during the day... why? so the total number of cycles per day is constant... why? so the electric clocks are always on time when the alarm goes off in the morning... otherwise the error accumulated in one year could be about 10 to 15 min or more.
3. Power factor is a consequence and not a cause... the two independent variables are active and reactive power. some control systems enable the units to keep a constant power factor... but the reason for it is to maintain the generator at the design power factor (usually 0.85 or 0.80) or better (higher).
When the dispatch requests the operator to raise or lower var to maintain the grid's voltage they are using copper of the generator to carry that load... i.e. increased heat generated.
The real danger of very low var (negative) is that you can hit the UEL (under excitation limit) which is normally a trip of the excitation system... otherwise the generator may skip a pole and fall "out of step" with very bad physical consequences for the generator due to the huge electromagnetic torques associated with these events.
HTH
saludos.
a.
abeltio,
Thanks for the explanation. That is what I am trying to come to understand. What do they physically do to make the copper in the generator carry the load as you put it.
Or, said differently, what they do when they make a power factor shift at the power station to account for power factor changes on the system.
The one thing I do remember about vars from the EE classes I had to take as a ME was that it involved heating up the conductors, but I can't remember why.
And, I do well understand the dangers of under excitation and the potential for 'slipping a pole' and the devastation that can happen there. I was once a service engineer for a major turbine/generator OEM, but on the mechanical side. We had to fix the devastation when it (rarely) occurred.
In my thread above, Barrie66 did not understand that I was describing a hypothetical system where the load suddenly shifted from reactive power to resistive power. Forget about the real world where load begins to drop off when factories shut down at the end of the shift. Convert all their reactive load from their factory motor driven machinery to resistive load heating their houses and food, and tell me what the power plant does to accommodate the shift in power factor from lagging to unity.
Another question; is part of South America 50 hz? Somehow, I thought all of our hemisphere was 60 Hz, but I don't know how I got that.
I described in one of the other threads that was discussing this topic about older systems that I used to work on where they maintained their system frequency by having two clocks on the control board, one connected to their system, (usually a municipality or plant with their own power station) and one connected to the grid that they only tied to when their system tripped or was down.
rmw
And, no, I am no longer in South America, but I will be there again within a couple of months. I'll be fighting the Spanish keyboards again I'm sure.
In Brazil, the larger cities are 60Hz but I think some areas are 50Hz.
Not so fast amigo Abeltio. We should be careful to generalize for one particular isolate case.
We know that is not economical to use the GT to produce vars. Maybe the reason of this operating mode is the abundant hydropower at a particular season.
Uruguay electrical energy generation is highly dependent on the weather conditions. Therefore, the optimal operating mode for generating or consuming var is based on economic decisions and availability of hydro versus thermal power.
Regarding system frequency, Argentina, Chile, Bolivia, Paraguay, Uruguay operate a 50 Hz, while the rest of the continent primarily operate at 60 Hz.
[blue]NOTE: Even though larger numbers of consumer are served from 60Hz, most countries in SA are under the IEC influence. I remember how difficulties was to convince the engineers in Chile to accept the first ring bus and the struggling to bring 500 kV breakers in Argentina. Most local engineers are not familiar with dead-tank breakers used typically in the ANSI marketplace[/blue]
cuky2000,
are we sure we r talking about the same thing? in my post i stated that the GT is not run to produce vars... it is used to bring the generator to synch speed, synch to the grid and then the GT is SHUT DOWN.
btw the synch condenser installation in uruguay is running in synch condenser mode 50% of the time... i know i commissioned the plant.
rmw,
from the operator's point of view it is very simple...
when the excitation control system of the turbine is set to
"nothing" the excitation is DROOPING to the voltage of the grid: i.e. if the voltage drops the excitation increases generating more vars... conversely if the voltage of the line increases the excitation decreases.
in case the excitation control system of the turbine is set to "power factor control": it controls the power factor to a certain setpoint... this is done some times to protect the generator... but does not help the grid.
the other possibility is to set the excitation control to: "var control" then the vars are kept constant to whatever the setpoint is...
this is sometimes required by the grid dispatcher to manage the line voltage.
to carry the load in the copper of the generator given a certain copper section: the oem calculates how many var and mw the generator can carry at a certain cooling condition which could be H2 pressure or cold air temperature depending on the generator.
the result of this calculations are the CAPABILITY CURVES that give the combination of var / mw the generator can carry.
don't keep asking because i do not know much more... i am mechanical too!
saludos.
a.
abeltio,
Thanks, you are miles ahead of me, or is that KM's? It has been several lifetimes since I learned all that stuff, and while most of my work is in the vicinity of the generator's control, I am normally much too busy trying to get mechanical stuff working so that the generator can produce power.
I am trying to brush up on what I learned a long time ago, and haven pretty much taken for granted since then since I didn't need to pay any attention to that part of the plant.
You have been very helpful and I appreciate it.
rmw