Assuming that all the pumps are equal capacity, parallel piped on a common header and individually able to be run in place of any other pump...
1. N+1
2. 2N (more common than N+N)
3. N+1
N refers to the number of pumps (or equipment in general) required to meet the design flow (load etc).
N+1 indicates this many pumps and one spare. It could be one pump or a hundred, with one spare. Obviously with 100 duty pumps you might want a few more spares, with N+2, 3, 4 etc. resulting.
2N is a much more substantial deal and refers to a spare for every pump, but is often realized with separate parallel plant so that pipework and accessories and even major plant are replicated. Two pumps, one duty and one spare are usually termed N+1 for this reason.
You can also group redundant equipment - with say one spare for each of four groups of equipment (makes sense in a fan or crac unit context) being 4(N+1).