PEDARRIN2
Mechanical
- Oct 1, 2003
- 1,287
This question is geared toward building natural gas regulators where the inlet presssure is likely to max at 10 psig and be regulatored down to 7 in w.c. Flows are going to be on the low end, likely maxing out at around 10,000 cfh.
I am familiar with natural gas equipment turn down ratios but have never seen the term be related to the regulators. With equipment, this is always a flow parameter, but doing a little research, I have found guidance that indicates it to be the ratio of the inlet/outlet pressure. Not sure if that is absolute pressures, but with 10 psig maximum and regulate down to about 7 in w.c. (0.25 psig). So that would be a 40:1 turn down ratio if using pressure.
But other guidance indicates it to be the flow ratio.
I have seen references that indicates the regulator should be sized for 10:1 turn down flow ratio. For a building, that might also be difficult since the regulator may be required to control pressure at flows of 120 cfh (water heater) all the way up to 10,000+ cfh (boilers, kitchen equipment, water heaters) which would exceed the 10:1 ratio.
A lot of the regulators I commonly specify do not even mention turn down ratio in their literature.
Any guidance would be appreciated.
I am familiar with natural gas equipment turn down ratios but have never seen the term be related to the regulators. With equipment, this is always a flow parameter, but doing a little research, I have found guidance that indicates it to be the ratio of the inlet/outlet pressure. Not sure if that is absolute pressures, but with 10 psig maximum and regulate down to about 7 in w.c. (0.25 psig). So that would be a 40:1 turn down ratio if using pressure.
But other guidance indicates it to be the flow ratio.
I have seen references that indicates the regulator should be sized for 10:1 turn down flow ratio. For a building, that might also be difficult since the regulator may be required to control pressure at flows of 120 cfh (water heater) all the way up to 10,000+ cfh (boilers, kitchen equipment, water heaters) which would exceed the 10:1 ratio.
A lot of the regulators I commonly specify do not even mention turn down ratio in their literature.
Any guidance would be appreciated.