jreit
Structural
- May 2, 2014
- 95
Hello. I usually don't design with wood so I'm a little out of my depth here. I have a timber lagging design that I'm doing a review on and the EOR is checking the bending stress for a 3x4 roughcut beam. However, he's using the actual span of 6'. From NDS 2015, Section 3.3.3.5 it appears that the bending moment should be calculated using an effective span length, le, rather than the span (lu) of 6'. When I made the comment, he stated that this effective span length does not apply for flatwise use.
I can't find anything in the code that explicitly states that.
9.4.1(a) states the design span for flatwise bending should be the distance between supports. It doesn't say effective span length which is what 3.3.3.5 refers to.
I wanted to check what the normal practice was before replying to him.
I can't find anything in the code that explicitly states that.
9.4.1(a) states the design span for flatwise bending should be the distance between supports. It doesn't say effective span length which is what 3.3.3.5 refers to.
I wanted to check what the normal practice was before replying to him.