Dan6779
Electrical
- May 12, 2018
- 3
This is my first posting here. I work as an electrical inspector.
NEC 110. 24 requires service equipment for other than dwelling units to be marked with the maximum available fault current. In my state, we consider apartment buildings with more than two apartments to be an "other than dwelling unit." I have been requiring this to be posted at service mains.
Some apartment buildings are set up with main breakers located at the individual apartments, while others have meter/mains set up at a central location. In designs where the mains are located in individual apartments it is easy to determine the available fault current when you know the size and length of the feeders. Where am a bit perplexed, is the times when the mains are located close to the service main.
Say we have 40 unit apartment building, and the service has an available fault current of 30K. The service has a 65K rated main, so we are fine there. The electrician installs meter/mains rated for 10K.
My question is, do all these feeders have a bleeding affect on the available fault current? Can the 10K meter/mains stay?
NEC 110. 24 requires service equipment for other than dwelling units to be marked with the maximum available fault current. In my state, we consider apartment buildings with more than two apartments to be an "other than dwelling unit." I have been requiring this to be posted at service mains.
Some apartment buildings are set up with main breakers located at the individual apartments, while others have meter/mains set up at a central location. In designs where the mains are located in individual apartments it is easy to determine the available fault current when you know the size and length of the feeders. Where am a bit perplexed, is the times when the mains are located close to the service main.
Say we have 40 unit apartment building, and the service has an available fault current of 30K. The service has a 65K rated main, so we are fine there. The electrician installs meter/mains rated for 10K.
My question is, do all these feeders have a bleeding affect on the available fault current? Can the 10K meter/mains stay?