OhioAviator
Electrical
- Sep 8, 2003
- 123
Situation:
Small industrial facility, two-story building with two motor control centers and one 400Amp main-lug panelboard located on the second floor. Motor control centers are rated 2,000Amp main bus and are also main-lug only.
Located approximately 30 feet away from building at ground level is a 3,000KVA outdoor unit substation incorporating a GE outdoor non-walk-in switchgear lineup with six (6) AKD-10 circuit breakers. Substation is metalclad so there is no substation fence. The two motor control centers and the 400Amp MLO panel, and the underground feeder conductors serving them, are each protected by it's own AKD-10 circuit breaker in the substation. All circuit breakers are clearly marked indicating the load each serves. The substation is fed from an outdoor PowerVac switchgear lineup. All equipment is customer owned with the electric utility point of service located at the other end of the property at a pole-top recloser.
Question: Does this installation as described violate Article 230.70(A)(1) of the 2005 National Electrical Code? The local AHJ seems to think so and is asking us to replace the 400Amp MLO panel with a main breaker panel and also install a 2,000Amp main circuit breaker in each motor control center. If not, then any suggestions on how we can persuade the AHJ to change his mind?
Thanks in advance for your help.