iceworm
Electrical
- Jun 19, 2009
- 215
New section to the NEC. It is not effective until 2020, so lots of time. The particular section I am looking at is "Energy-reducing maintenance switching".
240.67 Arc Energy Reduction. Where fuses rated 1200 A or higher are installed, 240.67(A) and (B) shall apply. This
requirement shall become effective January 1, 2020.
(A) Documentation. Documentation shall be available to those authorized to design, install, operate, or inspect the
installation as to the location of the fuses.
(B) Method to Reduce Clearing Time. A fuse shall have a clearing time of 0.07 seconds or less at the available arcing
current, or one of the following shall be provided:
(1) Differential relaying
(2) Energy-reducing maintenance switching with local status indicator
(3) Energy-reducing active arc flash mitigation system
(4) An approved equivalent means
Informational Note No. 1: An energy-reducing maintenance switch allows a worker to set a
disconnect switch to reduce the clearing time while the worker is working within an arc-flash
boundary as defined in NFPA 70E -2015, Standard for Electrical Safety in the Workplace, and then to
set the disconnect switch back to a normal setting after the potentially hazardous work is
complete.
Informational Note No. 2: An energy-reducing active arc flash mitigation system helps in reducing
arcing duration in the electrical distribution system. No change in the disconnect switch or the
settings of other devices is required during maintenance when a worker is working within an arc
flash boundary as defined in NFPA 70E -2015, Standard for Electrical Safety in the Workplace.
Informational Note No. 3: IEEE 1584, IEEE Guide for Performing
Arc Flash Hazard Calculations, is one of the available methods that
provides guidance in determining arcing current.
Bold emphasis is mine)
I'm at a complete loss as to the physics about how one might do this.
Anybody got any clues?
Iceworm
Harmless flakes working together can unleash an avalanche of destruction
240.67 Arc Energy Reduction. Where fuses rated 1200 A or higher are installed, 240.67(A) and (B) shall apply. This
requirement shall become effective January 1, 2020.
(A) Documentation. Documentation shall be available to those authorized to design, install, operate, or inspect the
installation as to the location of the fuses.
(B) Method to Reduce Clearing Time. A fuse shall have a clearing time of 0.07 seconds or less at the available arcing
current, or one of the following shall be provided:
(1) Differential relaying
(2) Energy-reducing maintenance switching with local status indicator
(3) Energy-reducing active arc flash mitigation system
(4) An approved equivalent means
Informational Note No. 1: An energy-reducing maintenance switch allows a worker to set a
disconnect switch to reduce the clearing time while the worker is working within an arc-flash
boundary as defined in NFPA 70E -2015, Standard for Electrical Safety in the Workplace, and then to
set the disconnect switch back to a normal setting after the potentially hazardous work is
complete.
Informational Note No. 2: An energy-reducing active arc flash mitigation system helps in reducing
arcing duration in the electrical distribution system. No change in the disconnect switch or the
settings of other devices is required during maintenance when a worker is working within an arc
flash boundary as defined in NFPA 70E -2015, Standard for Electrical Safety in the Workplace.
Informational Note No. 3: IEEE 1584, IEEE Guide for Performing
Arc Flash Hazard Calculations, is one of the available methods that
provides guidance in determining arcing current.
Bold emphasis is mine)
I'm at a complete loss as to the physics about how one might do this.
Anybody got any clues?
Iceworm
Harmless flakes working together can unleash an avalanche of destruction