cherryg222
Electrical
- Apr 6, 2016
- 23
Recently read an article in EC&M from 2007 which said:
When correcting conductor ampacity for elevated ambient temperature, the correction factor used for THHN conductors is based on the 90°C rating of the conductor, based on the conductor ampacity listed in the 90°C column of Table 310.16 [110.14(C)].
When adjusting conductor ampacity, the ampacity is based on the temperature insulation rating of the conductor as listed in Table 310.16, not the temperature rating of the terminal [110.14(C)].
The first statement is easy and logical. The second statement requires an explanation. Why would we not use 75degC Column ampacity values for 75degC rated terminals, typically in LV?