NEC Ampacity Tables

Status
Not open for further replies.

nightfox1925

Electrical
Apr 3, 2006
567
Sirs, which NEC Ampacity Tables I could suitably use to size up XLPE power cables directly buried to earth? I wish to refrain using specific cable manufacturer catalogues since we do not know the cable vendor at this point. Is there an NEC ampacity table applicable to XLPE insulated 3 core cables?

GO PLACIDLY, AMIDST THE NOISE AND HASTE-Desiderata
 
Replies continue below

Recommended for you

600VAC and 4.16kV application. Direct burial and above ground in tray applications. I find it more convenient to use the code so as not to be dependent to any manufacturer values, specially during conceptual design.