buzzp
Electrical
- Nov 21, 2001
- 2,032
Our customer decided at the last minute to put in a transfer switch (manual-really a contactor), non service entrance rated (no overcurrent protection). They want to put it in after the service transformer and metering but before the disconnect. I have researched this and there seems to be some confusion in interpreting 230.82 and 230.94. From an engineering standpoint, the manual transfer switch is not protected since the overcurrent protection is after it. Based on this alone, makes this idea bad in my opinion. However, I believe the utility has cut-outs on the primary of their transformer.
In any case, is this configuration allowed by the NEC? Is it allowed since the transfer switch is UL listed and part of the requirement to maintain the listing is to provide OC protection?
Any help would be appreciated. Sorry if I posted in the wrong area. Thank you!
In any case, is this configuration allowed by the NEC? Is it allowed since the transfer switch is UL listed and part of the requirement to maintain the listing is to provide OC protection?
Any help would be appreciated. Sorry if I posted in the wrong area. Thank you!