NEC understanding about continuous load that have been decreased by demand load? 1

Status
Not open for further replies.

Askarel27

Electrical
Joined
Dec 23, 2013
Messages
13
Location
SA
This question is for code book understanding. Article 220 is reasonably clear as to the definition of continuous and non-continuous loads and how they affect the size of feeders and services.
My question is,
"How does the NEC expect the designer/engineer to treat the loads that have been decreased due to a Demand Factor elsewhere in the Code?"
A very clear example of my question comes from Table 220-20, Kitchen Equipment. After a demand factor of 65% is applied to six pieces of kitchen equipment, is this demand load considered continuous or non-continuous?
 
The demand factor is for sizing services and feeders. Your service transformer size or feeder size is allowed to be 65% of total load, but you still have to size your individual branch circuits for the kitchen equipment based on the total continuous/non-continuous load requirements.