NEC 250.36 covers high impedance grounding, and 250.36.a states that the ground reference has to be to a neutral. It says:
"The grounding impedance shall be installed between the grounding electrode conductor and the system neutral. When a neutral is not available, the grounding impedance shall be installed between the grounding eledctrode conductor and the neutral derived from a grounding transformer."
This wording broaches on disallowing completely ungrounded delta or wye secondaries, and further disallows high impedance corner grounding of deltas. I know most people do not like high impedance grounded systems, but if you can ignore that issue, does anyone want to comment if the NEC has a valid reason for the above paragraph?
"The grounding impedance shall be installed between the grounding electrode conductor and the system neutral. When a neutral is not available, the grounding impedance shall be installed between the grounding eledctrode conductor and the neutral derived from a grounding transformer."
This wording broaches on disallowing completely ungrounded delta or wye secondaries, and further disallows high impedance corner grounding of deltas. I know most people do not like high impedance grounded systems, but if you can ignore that issue, does anyone want to comment if the NEC has a valid reason for the above paragraph?