We have 2 Yd1 transformers in parallel. (20MVA, 66/11kV each) The secondary side of each transformer is earthed with a NEC. (zig-zag transformer, 400A, 10sec) Our problems start with earth-faults on the downstream feeders. Sometimes, when a fault occurs, the NECs trip on top oil temperature. (Earth fault relays don't have time to operate) But, if you touch the NEC, it is still cold.
Now my question is:
Can the mechanical vibration in the NEC during a fault condition operate the temp relay?(Temp-relay is situated on NEC and has mercury contacts) Just have to mention the system is relatively old, the NECs are solidly grounded and not through resistors. We plan to do some earth tests to ensure the ground connection of both NECs are still good, although both show temp flags (trippings)
Or am I missing something regarding oil temperature?
Thanx
Regards
Ralph
Now my question is:
Can the mechanical vibration in the NEC during a fault condition operate the temp relay?(Temp-relay is situated on NEC and has mercury contacts) Just have to mention the system is relatively old, the NECs are solidly grounded and not through resistors. We plan to do some earth tests to ensure the ground connection of both NECs are still good, although both show temp flags (trippings)