Need Rotation meter for VFDs

Status
Not open for further replies.

haze10

Electrical
Jan 13, 2006
81
Can anyone recommend a phase rotation meter that will work on PWM VFD outputs. My AEMC #PMR-1 meter seems to go nuts when I connect it. I was thinking one of the old fashion rotating motor type meters would work. Anyone solve this problem?
 
Replies continue below

Recommended for you

The old fashioned electromechanical rotation meters should work fine, I used them as demos to show instant reversal capabilities of VFDs years ago (before people readily accepted the concept). Here's one similar to what I had.