For power transformer protection of a standard Delta-wye radially-fed transformer, is it normal to utilize negative sequence protection to gain sensitivity? What is commonly recommended for settings sensitivity to avoid inadvertent trips? As in, should it be set to pickup at 50% of expected maximum load current or something similar?
Where else is it common to see negative sequence protection and where is it a good idea to avoid? I don't see this utilized very often.
For zero-sequence protection upstream from a radially connected transformer, I've seen very sensitive settings applied. The Delta-wye transformer should have no zero sequence current flow for low-side faults, so greater sensitivity can be achieved for high side faults. What are some things to consider before settings zero sequence elements too sensitive? Non-transposed lines, CT saturation for low-side faults, ??
Thanks
Where else is it common to see negative sequence protection and where is it a good idea to avoid? I don't see this utilized very often.
For zero-sequence protection upstream from a radially connected transformer, I've seen very sensitive settings applied. The Delta-wye transformer should have no zero sequence current flow for low-side faults, so greater sensitivity can be achieved for high side faults. What are some things to consider before settings zero sequence elements too sensitive? Non-transposed lines, CT saturation for low-side faults, ??