I need to design a negative pressure room with 30Pa. There are 2 safety booth in the room and each booth will have one exhaust fan.
I mention the following parameters for your convenience:
The room volume: 56.64 m3
Room ACPH required: 20
DP: -30PA
Adjacent room: warehouse and outside wall
I want to use ceiling mounted split AC. Can the split AC maintain 20ACPH by self circulation?
As the adjacent room is warehouse, so I would like to add a fresh air duct from outside environment to support the exhaust fan. Because, I think there will not enough air to support the exhaust fan. The exhaust fan should provide 20ACPH as design condition.
So, I think about the calculation like this: EA= FA(from environment)+ Infiltration(leakage from door); is that correct??
When the safety booth is off,the room also should maintain 20ACPH.
For fresh air, the outside design condition in summer is 35 degree and 90% RH
The room air= 56.64*20= 1132.8 CMH
The infiltration air will be Q=2610A√△P= 232.03 CMH by considering 1500mm door width and 10mm gap height.
How to estimate the EA and FA fan size? Should I consider the room volume like kitchen exhaust fan design? So, what about the fresh air?
Could anyone please give me some comments about the design issue.
Thanks
I mention the following parameters for your convenience:
The room volume: 56.64 m3
Room ACPH required: 20
DP: -30PA
Adjacent room: warehouse and outside wall
I want to use ceiling mounted split AC. Can the split AC maintain 20ACPH by self circulation?
As the adjacent room is warehouse, so I would like to add a fresh air duct from outside environment to support the exhaust fan. Because, I think there will not enough air to support the exhaust fan. The exhaust fan should provide 20ACPH as design condition.
So, I think about the calculation like this: EA= FA(from environment)+ Infiltration(leakage from door); is that correct??
When the safety booth is off,the room also should maintain 20ACPH.
For fresh air, the outside design condition in summer is 35 degree and 90% RH
The room air= 56.64*20= 1132.8 CMH
The infiltration air will be Q=2610A√△P= 232.03 CMH by considering 1500mm door width and 10mm gap height.
How to estimate the EA and FA fan size? Should I consider the room volume like kitchen exhaust fan design? So, what about the fresh air?
Could anyone please give me some comments about the design issue.