Oct 14, 2022 #1 RENEET Electrical Oct 14, 2022 1 0 0 US If you have a breaker with a 4 home nema pad can you use only two holes on the pad? Like I want to use a two hole connector on a 4 hole pad.
If you have a breaker with a 4 home nema pad can you use only two holes on the pad? Like I want to use a two hole connector on a 4 hole pad.
Oct 14, 2022 1 #2 jghrist Electrical Jul 16, 2002 4,204 0 36 US Yes, as long as you do not exceed the rating of the two hole connector (which is the ampacity of the conductor at the rated terminal temperature). Upvote 0 Downvote
Yes, as long as you do not exceed the rating of the two hole connector (which is the ampacity of the conductor at the rated terminal temperature).