If you have a breaker with a 4 home nema pad can you use only two holes on the pad? Like I want to use a two hole connector on a 4 hole pad.
 
Replies continue below

Recommended for you

Yes, as long as you do not exceed the rating of the two hole connector (which is the ampacity of the conductor at the rated terminal temperature).
 