loicalset
Electrical
- May 1, 2007
- 25
Hello,
I am looking to design a NEMA 8 enclosure and would like to know if anybody has experience with what exactly the spec means. I can't decipher if it means the electronics enclosure will be filled with oil or if it will be submerged in oil. Oil submersion makes more sense to me, but I haven't seen that in practice yet, so I don't know if that is something standard. Any tips?
The spec reads, "Type 8 enclosures and enclosed devices are arranged such that all arcing contacts, connections, and the like are immersed in oil. Arcing is confined under the oil such that it will not ignite an explosive mixture of the specified gases (hydrogen, cyclopropane, gasoline, acetlyene, etc) in internal spaces above the oil or in the atmosphere surrounding the enclosure. Enclosed heat generating devices shall not cause external surfaces t oreach temperatures capable of igniting explosive gas-air mixtures in the surrounding atmosphere. Type 8 enclosures:
a. Provide, by oil immersion, a degree of protection to a hazardous gas environment from operation of internal equipment.
...
c. Withstand a series of operation design tests with oil levels arbitrarily reduced and with flammable gas-air mixtures introduced above the oil.
That's pretty much it. Ideas?
I am looking to design a NEMA 8 enclosure and would like to know if anybody has experience with what exactly the spec means. I can't decipher if it means the electronics enclosure will be filled with oil or if it will be submerged in oil. Oil submersion makes more sense to me, but I haven't seen that in practice yet, so I don't know if that is something standard. Any tips?
The spec reads, "Type 8 enclosures and enclosed devices are arranged such that all arcing contacts, connections, and the like are immersed in oil. Arcing is confined under the oil such that it will not ignite an explosive mixture of the specified gases (hydrogen, cyclopropane, gasoline, acetlyene, etc) in internal spaces above the oil or in the atmosphere surrounding the enclosure. Enclosed heat generating devices shall not cause external surfaces t oreach temperatures capable of igniting explosive gas-air mixtures in the surrounding atmosphere. Type 8 enclosures:
a. Provide, by oil immersion, a degree of protection to a hazardous gas environment from operation of internal equipment.
...
c. Withstand a series of operation design tests with oil levels arbitrarily reduced and with flammable gas-air mixtures introduced above the oil.
That's pretty much it. Ideas?