structuraldan
Structural
- Jan 27, 2005
- 10
With the help of a senior engineer, I designed a large open bay steel warehouse building, 105' wide by 400' long by 45' high, and used steel joists and girders for framing. The joists are 105' long, 8' deep, moment resisting and have restrained top and bottom chords. Standard joist tables are not applicable due to roof slope and joist depth.
Due to these conditions, and use of LRFD design, we decided the best approach was to provide shear and moment envelopes for each joist design, instead of unfactored wind loads per joist tributary area. This would allow us more control as to what would be provided and provide best interpretation of design requirements. To assist, I also indicated envelopes are based on factored loads and sign convention for uplift on the drawings.
The contractor's fabricator insists on requesting net uplift load psf, "per SJI specification requirements" in the latest RFI. Coworkers in the office agree that not only the information provided on the drawings was more than sufficient for design, but required due to OUR design interpretation of the building system, vs. the joist designer's need for his component design. (Although an important one, presumably using ASD with stress increase allowance for wind forces.)
Is there a viable reason why the joist designer cannot use the information provided to size the joist members? (Also why is LRFD not adequately addressed in SJI?)
I'd like to get as many comments as soon as possible to give due consideration to the RFI. Thanks
Due to these conditions, and use of LRFD design, we decided the best approach was to provide shear and moment envelopes for each joist design, instead of unfactored wind loads per joist tributary area. This would allow us more control as to what would be provided and provide best interpretation of design requirements. To assist, I also indicated envelopes are based on factored loads and sign convention for uplift on the drawings.
The contractor's fabricator insists on requesting net uplift load psf, "per SJI specification requirements" in the latest RFI. Coworkers in the office agree that not only the information provided on the drawings was more than sufficient for design, but required due to OUR design interpretation of the building system, vs. the joist designer's need for his component design. (Although an important one, presumably using ASD with stress increase allowance for wind forces.)
Is there a viable reason why the joist designer cannot use the information provided to size the joist members? (Also why is LRFD not adequately addressed in SJI?)
I'd like to get as many comments as soon as possible to give due consideration to the RFI. Thanks