fieldy
Electrical
- Apr 22, 2004
- 2
I was listening to a conversation recently regarding the following situation (as I understand it).
Location - USA
Incoming 13.2kV:480/277Y Utility Feed to Normal side of an ATS, Emergency side of ATS is fed from a 480/277Y diesel powered genset.
ATS feeds a breaker, followed by a UPS.
The issue seems to be with the bonding of the neutral. The utility has their neutral bonded to ground out at the street, and the generator neutral is bonded to ground at the generator. There is also a bonding point between neutral and ground at the UPS.
Folks here are wondering if that UPS neutral to ground bonding point is a second bonding point that will now violate code, and create circulating currents under normal situations (bonded neutral at utility/generator as well as bonded neutral at UPS), and they want to break the neutral to ground bonding point at the UPS.
If I understand what I read in a post from last year: - as well as hearing what the UPS manufacturer had to say, the UPS is actually a separately derived source, so it needs to have its own bonding point. Additional information on the UPS is that the incoming neutral is directly connected to the output neutral.
Another issue with lifting the bond at the UPS is that the 4-pole ATS switch is a break-before-make arrangement. During a swap from Normal to Emergency, the UPS would be running without a ground reference for any 4-wire loads.
I would like to know what is the proper solution for this situation. Your time and effort is greatly appreciated.
Location - USA
Incoming 13.2kV:480/277Y Utility Feed to Normal side of an ATS, Emergency side of ATS is fed from a 480/277Y diesel powered genset.
ATS feeds a breaker, followed by a UPS.
The issue seems to be with the bonding of the neutral. The utility has their neutral bonded to ground out at the street, and the generator neutral is bonded to ground at the generator. There is also a bonding point between neutral and ground at the UPS.
Folks here are wondering if that UPS neutral to ground bonding point is a second bonding point that will now violate code, and create circulating currents under normal situations (bonded neutral at utility/generator as well as bonded neutral at UPS), and they want to break the neutral to ground bonding point at the UPS.
If I understand what I read in a post from last year: - as well as hearing what the UPS manufacturer had to say, the UPS is actually a separately derived source, so it needs to have its own bonding point. Additional information on the UPS is that the incoming neutral is directly connected to the output neutral.
Another issue with lifting the bond at the UPS is that the 4-pole ATS switch is a break-before-make arrangement. During a swap from Normal to Emergency, the UPS would be running without a ground reference for any 4-wire loads.
I would like to know what is the proper solution for this situation. Your time and effort is greatly appreciated.