I apologize in advance for my ignorance on this topic....
If a neutral bus is solidly grounded, yet the neutral bushing connected to that bus (on the transformer) has a BIL rating of 150 kV, do you still have to worry about neutral-to-ground clearances between the neutral bus and grounded steel on equipment (such as transformer tanks)?
It is my belief that you still have to maintain the 12 inch clearance required for 150 kV BIL. I believe this is the case because the "solidy grounded" connection of the neutral bus won't appear to be solidly grouded to high frequency surges and might cause unintended arc-overs. I think it would be a mistake to reduce that clearance. Am I wrong?
If a neutral bus is solidly grounded, yet the neutral bushing connected to that bus (on the transformer) has a BIL rating of 150 kV, do you still have to worry about neutral-to-ground clearances between the neutral bus and grounded steel on equipment (such as transformer tanks)?
It is my belief that you still have to maintain the 12 inch clearance required for 150 kV BIL. I believe this is the case because the "solidy grounded" connection of the neutral bus won't appear to be solidly grouded to high frequency surges and might cause unintended arc-overs. I think it would be a mistake to reduce that clearance. Am I wrong?