ThePunisher
Electrical
- Nov 7, 2009
- 384
We have a 200 A, 10 Seconds NGR applied into the 13.8/7.96 kV secondary wye transformer neutral.
The CEC 2018 rule 10-308.1).e says that it will "BE SIZED TO CONDUCT THE RATED CURRENT OF THE IMPEDANCE GRODUNING DEVICE..."
Does this mean that we would treat 200 A as continuous if the NGR is only rated for 10 seconds and our protection would trip it for less than 2 seconds?
Can I use the GF pickup time into consideration and calculate the size of conductor that can withstand 100 A for 2 seconds.
1. If I size like it was 200 A continuous, I would be using #1/0 AWG
2. If I use the cable withstand (XLPE, 8 kV , General Cable), using the attached short circuit withstand for 200 A at max 2 seconds, I can use #8 or #6 AWG which can withstand 200 A for 35 seconds and 89 seconds respectively. If I use #12 (minimum as per CEC), it can only withstand for 5.5 seconds, so I won't use it.
I appreciate everyone's experience and expertise.
Thank you very much
The CEC 2018 rule 10-308.1).e says that it will "BE SIZED TO CONDUCT THE RATED CURRENT OF THE IMPEDANCE GRODUNING DEVICE..."
Does this mean that we would treat 200 A as continuous if the NGR is only rated for 10 seconds and our protection would trip it for less than 2 seconds?
Can I use the GF pickup time into consideration and calculate the size of conductor that can withstand 100 A for 2 seconds.
1. If I size like it was 200 A continuous, I would be using #1/0 AWG
2. If I use the cable withstand (XLPE, 8 kV , General Cable), using the attached short circuit withstand for 200 A at max 2 seconds, I can use #8 or #6 AWG which can withstand 200 A for 35 seconds and 89 seconds respectively. If I use #12 (minimum as per CEC), it can only withstand for 5.5 seconds, so I won't use it.
I appreciate everyone's experience and expertise.
Thank you very much