lyledunn
Electrical
- Dec 20, 2001
- 122
In the 3phase and neutral 400v supply cables in an office block my simple (but recently calibrated) clamp meter is indicating considerably more current in the neutral than would have been expected with vectoral addition.
Now there are no problems as the neutral is of appropriate cross section, however, I was wondering if this is a result of harmonics due to the Switch mode power supply units that I guess are in much of the IT equipment.
I understand that in such a system it is possible for the rms neutral current to be 1.73 times the rms current in the phase conductors. This is really the first time I have come across this in practice. Has anyone else met with a similar problem? Is it likely that csa of neutrals is likely to be carefully considered in future instead of just selecting same csa as associated phase conductors for load? Regards,
Lyledunn
Now there are no problems as the neutral is of appropriate cross section, however, I was wondering if this is a result of harmonics due to the Switch mode power supply units that I guess are in much of the IT equipment.
I understand that in such a system it is possible for the rms neutral current to be 1.73 times the rms current in the phase conductors. This is really the first time I have come across this in practice. Has anyone else met with a similar problem? Is it likely that csa of neutrals is likely to be carefully considered in future instead of just selecting same csa as associated phase conductors for load? Regards,
Lyledunn