We have 4 generators star point grounded through the PT, 8 MVA each. Step up transformers 11/34,5 kV; 8 MVA; Delta-Wye; connected. These four groups paralleled on 34,5 kV bus and one synchronizing breaker connect the bus to the network. The question is we have just one neutral grounding resistor 66 ohm. We connect one of transformers while normal operation. If this grounded neutral transformer tripped in any case an automatic transfer system disconnect the resistor and connect to one of the operated transformer. Is there any inconvienent situation here.
Is there any possibilities to voltage increases between the Phase-Neutral of ungrounded transformers.
If you need more info please ask me.
zub.
We have 4 generators star point grounded through the PT, 8 MVA each. Step up transformers 11/34,5 kV; 8 MVA; Delta-Wye; connected. These four groups paralleled on 34,5 kV bus and one synchronizing breaker connect the bus to the network. The question is we have just one neutral grounding resistor 66 ohm. We connect one of transformers while normal operation. If this grounded neutral transformer tripped in any case an automatic transfer system disconnect the resistor and connect to one of the operated transformer. Is there any inconvienent situation here.