Neutral grounding of generator

Status
Not open for further replies.

siwan

Electrical
Nov 18, 2011
2
If multiple synchronous generator earthed through neutral grounding transformer located in same power house . Shall one generator neutral be earthed or all the generators ?

 
Replies continue below

Recommended for you

All should be grounded through a grounding transformer
 
It depends on how the generators are connected to the system. If there is a dedicated unit transformer for each generator, each needs its own grounding resistor. If the generators are directly connected to a common bus, you have more choices and decisions to make.
 