Posted this on another forum already, but figured I'd look for insight here as well. A customer of ours had the conductors that connect to their neutral grounding resistor burn up. The 480V system is configured as a high resistance grounded system that consists of loads and generation (landfill cogeneration). General one-line below.
Here's how the grounding is configured at the transformer:
Here's a few photo's of the failed equipment. As you can see, the conductors burned up near the resistor. The resistor seems to have not been severely damaged though.
I'm having trouble determining what what could have caused this. No other equipment damage was found and no faults could be located on the system. What could have caused the conductors to heat up enough to ignite? Does this look like it could have been a lightning strike?
Sequence of potentially related events:
[ol 1]
[li]At the beginning of Sept. there was a phase-phase fault on the 33kV utility system very close to where it connects to this system in question. The customer's generator was running at the time (exporting power to the grid) and tripped offline. Utility crews fixed the issue on their side. After that, the customer's genset wouldn't run, and it was found that a 12V actuator wasn't functioning. They replaced the actuator and everything went back to running normally.[/li]
[/ol]
[ol 2]
[li]About 2 weeks later, maintenance personnel noticed a burnt smell and damage at the NGR. A testing company was brought in to test the generator, transformer, and cables, and reported no issues found.[/li]
[/ol]
Right now, the system is energized with the neutral solidly grounded at the transformer. Everything seems to be running fine, but the customer has not brought the generator back online out of fear of possible damage.
A few interesting facts:
[ol 1]
[li]The system was originally designed & installed as a solidly grounded system. There are "neutral" conductors run from the transformer to the distribution equipment, and some 277V lighting loads exist.[/li]
[/ol]
[ol 2]
[li]At some point a second generator was added, which was supplied by a foreign manufacturer. The manufacturer of the second generator demanded that an NGR be installed, so it was, but apparently not properly. However, the second generator has since been permanently removed from the system.[/li]
[/ol]
Any ideas about what caused this?
Here's how the grounding is configured at the transformer:
Here's a few photo's of the failed equipment. As you can see, the conductors burned up near the resistor. The resistor seems to have not been severely damaged though.
I'm having trouble determining what what could have caused this. No other equipment damage was found and no faults could be located on the system. What could have caused the conductors to heat up enough to ignite? Does this look like it could have been a lightning strike?
Sequence of potentially related events:
[ol 1]
[li]At the beginning of Sept. there was a phase-phase fault on the 33kV utility system very close to where it connects to this system in question. The customer's generator was running at the time (exporting power to the grid) and tripped offline. Utility crews fixed the issue on their side. After that, the customer's genset wouldn't run, and it was found that a 12V actuator wasn't functioning. They replaced the actuator and everything went back to running normally.[/li]
[/ol]
[ol 2]
[li]About 2 weeks later, maintenance personnel noticed a burnt smell and damage at the NGR. A testing company was brought in to test the generator, transformer, and cables, and reported no issues found.[/li]
[/ol]
Right now, the system is energized with the neutral solidly grounded at the transformer. Everything seems to be running fine, but the customer has not brought the generator back online out of fear of possible damage.
A few interesting facts:
[ol 1]
[li]The system was originally designed & installed as a solidly grounded system. There are "neutral" conductors run from the transformer to the distribution equipment, and some 277V lighting loads exist.[/li]
[/ol]
[ol 2]
[li]At some point a second generator was added, which was supplied by a foreign manufacturer. The manufacturer of the second generator demanded that an NGR be installed, so it was, but apparently not properly. However, the second generator has since been permanently removed from the system.[/li]
[/ol]
Any ideas about what caused this?