OdessaEE
Electrical
- Jun 19, 2008
- 9
I think I already know the answer to this, but I will ask anyway.
A substation with a 10MVA 138KV/4160V Delta Wye transformer feeds our facility. The power company is planning to install a neutral grounding resistor during our next shutdown.
Here is where my question comes in. The transformer feeds our 4160V switchgear in the plant. A feeder for a 300KVA 4160/480V Wye Wye transformer comes off this switchgear. The transformer has an internal bonding jumper that is connected to both XO connections and is grounded to the plant grounding system. Will the neutral being grounded on the primary side of the transformer effectively make our neutral grounding system useless if we experienced a line to ground fault on the 4160V system?
A substation with a 10MVA 138KV/4160V Delta Wye transformer feeds our facility. The power company is planning to install a neutral grounding resistor during our next shutdown.
Here is where my question comes in. The transformer feeds our 4160V switchgear in the plant. A feeder for a 300KVA 4160/480V Wye Wye transformer comes off this switchgear. The transformer has an internal bonding jumper that is connected to both XO connections and is grounded to the plant grounding system. Will the neutral being grounded on the primary side of the transformer effectively make our neutral grounding system useless if we experienced a line to ground fault on the 4160V system?