Neutral in a UPS setup

Status
Not open for further replies.

Eclair

Electrical
Oct 14, 2007
12
US
Hi everyone

I have a UPS system that goes that way:

Inverter:
600V-120/208V transformer 3 wires going through a 3 pole breaker that makes the input of the UPS.

bypass:
600V-120/208V transformer 4 wire going through a 3 pole breaker that makes the input of the bypass. The neutral is not going through the breaker.

The bypass neutral is what that makes the neutral of the inverter at the output of the UPS.

My question: Does the neutral have to go through the breaker (4 pole breaker)?

I do know that the neutral cannot be wired alone and must be included into the 3 phase wire.

Thanks!
 
Replies continue below

Recommended for you

The neutral should not go through the breaker. Otherwise the UPS output will loose its ground reference if the breaker opens.
 