We have a wye grd - wye grd 12kV - 480V transformer. The utility lines are 12kV 3 wire and the neutral of the primary windings are grounded through a potential transformer (PT) at the transformer pole. The neutral of the secondary is grounded the main 480V panel. This is a generator facility, so the output of the primary PT is connected to a 59N relay per utility's requirement in order to detect ground fault on the utility side and disconnect the generator, so it does not feed into the fault.
However, we are seeing significant neutral voltage on the PT. We measured 3,000V from the neutral of the wye on the primary side to ground. On the 59N relay, we are seeing ~30V which comprises of almost pure third harmonic voltage.
The L-L voltages on the 480V side looks normal around 460-470 V with 2% VTHD but the L-N voltages on the 480V side shows very distorted waveform with 40% VTHD, we are seeing about 120V of third harmonic voltage on 277V L-N.
This is all when the transformer is unloaded and generator cannot run because it keeps tripping intermittently from 59N.
Anyone has any ideas what could be causing such significant third harmonic voltage and neutral overvoltage?
Utility says they are not detecting any ground fault on the 12kV incoming lines. We checked the grounding on both primary and secondary side of the transformer and everything looks normal.
Thank you.
We have a wye grd - wye grd 12kV - 480V transformer. The utility lines are 12kV 3 wire and the neutral of the primary windings are grounded through a potential transformer (PT) at the transformer pole. The neutral of the secondary is grounded the main 480V panel. This is a generator facility, so the output of the primary PT is connected to a 59N relay per utility's requirement in order to detect ground fault on the utility side and disconnect the generator, so it does not feed into the fault.
However, we are seeing significant neutral voltage on the PT. We measured 3,000V from the neutral of the wye on the primary side to ground. On the 59N relay, we are seeing ~30V which comprises of almost pure third harmonic voltage.
The L-L voltages on the 480V side looks normal around 460-470 V with 2% VTHD but the L-N voltages on the 480V side shows very distorted waveform with 40% VTHD, we are seeing about 120V of third harmonic voltage on 277V L-N.
This is all when the transformer is unloaded and generator cannot run because it keeps tripping intermittently from 59N.
Anyone has any ideas what could be causing such significant third harmonic voltage and neutral overvoltage?
Utility says they are not detecting any ground fault on the 12kV incoming lines. We checked the grounding on both primary and secondary side of the transformer and everything looks normal.