seamus000
Electrical
- Dec 1, 2000
- 6
Have reviewed previous postings, but...
120/240 3p/4w system feeding 120/240 distribution panel (all 1p loads, not particularly balanced, and a pump control panel (2 motors powered from 3 phases with no neutral connection, 120v 1p control equipment powered from A-leg to neutral from power company transformer.)
1)What are the rules (NEC) for sizing the neutral conductor? particularly from the power company transformer through to the dist panel and to the PCP?
2) is this concidered to be a current-carrying conductor? does it need to be considered in sizing all four conductors back to transformer (in conduit)? i.e. do i need to derate ampacities by 80%?
Thank you in advance.
120/240 3p/4w system feeding 120/240 distribution panel (all 1p loads, not particularly balanced, and a pump control panel (2 motors powered from 3 phases with no neutral connection, 120v 1p control equipment powered from A-leg to neutral from power company transformer.)
1)What are the rules (NEC) for sizing the neutral conductor? particularly from the power company transformer through to the dist panel and to the PCP?
2) is this concidered to be a current-carrying conductor? does it need to be considered in sizing all four conductors back to transformer (in conduit)? i.e. do i need to derate ampacities by 80%?
Thank you in advance.