RichardTaylor
Electrical
- Jul 3, 2003
- 4
I work for a UK distribution network operator.
We fit Neutral Voltage Displacement protection on our 33/11kV delta-star transformers in order to detect and clear earth-faults backfed from the 11kV busbars.
Traditionally, the NVD protection signal has been derived from a star-connected set of capacitor bushings on the 33kV side of the transformer, feeding into an Edgcumbe Peebles type NVD101 relay via a small transformer / rectifier unit. The capacitor bushings on modern transformers have a value of 150pF.
These relays are set to detect a 33kV system neutral displacement of 5kV.
We have now stopped using the NVD101 relays, as these are proving unreliable and expensive, and started using Alstom MVTU13 relays, until these became obsolete. We are now using Alstom P921 relays.
The question I would like to ask is whether anyone else is using this arrangement? If so, I would like some advice on settings for the relay.
Various people in our organisation have calculated settings, but have come up with settings between 1V and 14V. (The minimum setting available is 5V.)
We have done some injection tests, which suggest that a setting of 5V is about right, but I would like some theoretical cofirmation of this.
Does anyone use any other type of relay?
Can give further details if required.
We fit Neutral Voltage Displacement protection on our 33/11kV delta-star transformers in order to detect and clear earth-faults backfed from the 11kV busbars.
Traditionally, the NVD protection signal has been derived from a star-connected set of capacitor bushings on the 33kV side of the transformer, feeding into an Edgcumbe Peebles type NVD101 relay via a small transformer / rectifier unit. The capacitor bushings on modern transformers have a value of 150pF.
These relays are set to detect a 33kV system neutral displacement of 5kV.
We have now stopped using the NVD101 relays, as these are proving unreliable and expensive, and started using Alstom MVTU13 relays, until these became obsolete. We are now using Alstom P921 relays.
The question I would like to ask is whether anyone else is using this arrangement? If so, I would like some advice on settings for the relay.
Various people in our organisation have calculated settings, but have come up with settings between 1V and 14V. (The minimum setting available is 5V.)
We have done some injection tests, which suggest that a setting of 5V is about right, but I would like some theoretical cofirmation of this.
Does anyone use any other type of relay?
Can give further details if required.