For those of you who revel in odd problems, here is a new one, for me anyway.
Customer called me for consult on problems starting a 20HP 460V motor on a dust collection blower (squirrel cage). They had been using a Y-Delta starter, but transition spikes damaged the motor so they converted to X-Line (DOL). Motor was now drawing LRA and tripping the OL relay before the fan got up to full speed. It had started fine with the Y-D starter, so I knew the motor must have enough torque to get it started, but I was puzzled as to why it no longer worked just from conversion to X-Line. Thoroughly checked motor and connections (thinking they had configured the windings wrong), no errors. Motor started and ran fine uncoupled, pulled 7.0A at full speed which seemed relatively normal for an unloaded 3550RPM motor. Recoupled and tripped again on start attempt. Choked off the outlet thinking that X-Line coupled the fan load quicker than Y-D had, so the load was possibly coming on too soon. Wrong again. Tried increasing OL to Class 20. No help. Finally bypassed OL all together and got it to start, but noticed that it was sucking in the inlet ducts!
When they had removed the motor for rework, the mechanics put the belt drive sheaves in reverse position, so instead of a 2:1 ratio from fan to motor so as to make the fan run at 1775 RPM, it was attempting to drive the fan at 7100RPM! The poor little motor just didn't have the kahounas to do it...
Occam's razor strikes again.
Customer called me for consult on problems starting a 20HP 460V motor on a dust collection blower (squirrel cage). They had been using a Y-Delta starter, but transition spikes damaged the motor so they converted to X-Line (DOL). Motor was now drawing LRA and tripping the OL relay before the fan got up to full speed. It had started fine with the Y-D starter, so I knew the motor must have enough torque to get it started, but I was puzzled as to why it no longer worked just from conversion to X-Line. Thoroughly checked motor and connections (thinking they had configured the windings wrong), no errors. Motor started and ran fine uncoupled, pulled 7.0A at full speed which seemed relatively normal for an unloaded 3550RPM motor. Recoupled and tripped again on start attempt. Choked off the outlet thinking that X-Line coupled the fan load quicker than Y-D had, so the load was possibly coming on too soon. Wrong again. Tried increasing OL to Class 20. No help. Finally bypassed OL all together and got it to start, but noticed that it was sucking in the inlet ducts!
When they had removed the motor for rework, the mechanics put the belt drive sheaves in reverse position, so instead of a 2:1 ratio from fan to motor so as to make the fan run at 1775 RPM, it was attempting to drive the fan at 7100RPM! The poor little motor just didn't have the kahounas to do it...
Occam's razor strikes again.