Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

New slab and equipment pad; pour together?

Status
Not open for further replies.

StructureMan44

Structural
Dec 10, 2014
201
A large area new 8" thick slab will support curbs, 6" housekeeping pads, and concrete piers. Would these be poured separately because of the difficulty in forming a curb, slab, or pier on top of a wet floor? I'm used to roughing the slab and doweling in curbs, pads, etc. on an existing slab but because the slab is new can the rebar for the slab, pads, etc. be placed integrally with the slab rebar.
 
Replies continue below

Recommended for you

Typically they're poured separately. Roughing is good if you need it but the dowels can handle plenty.

Sometimes contractors like to post install the dowels instead of casting in. Makes it easier to finish, especially when there are a lot of them.
 
Can be done either way, but separately is the most common practice. For the curbs, assuming they are of substantial length, you may need more reinforcing than you might think to control restraint shrinkage cracking.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor