Hotwheels1
Petroleum
- May 30, 2020
- 4
Hi Community!
We are in the process of designing the fire protection system for a gasoil and gasoline storage tank farm. The code followed is NFPA 11 and the system in question are "the Low-level foam discharge outlets for diked areas".
The tank farm will consist of 6 gasoil tanks and 6 gasoline tanks. See image below for simple sketch of arrangement.
Secondary spill containment will consist of external bund wall of 1.8m high (Black Line in Image), with 0.5m tall intermediate bund walls separating each tank (Red Line in Image).
When applying the application rate of 4.1 L/min/m2 for AFFF (NFPA 11, Table 5.7.3.2), we are debating whether to apply the foam to the smaller intermediate net bunded area per tank (E.g. Bund Area A), or do we apply it to the overall full tank farm net bund area for all 6 tanks (Bund Area A+B+C+D+E+F)?
Of course the water requirements for the smaller intermediate bund area is considerably more cost effective.
Further info:
Each tank will be fitted with fixed top foam pourers and shell cooling sprinkler systems, supplemented by foam and fire water hose streams.
We are in the process of designing the fire protection system for a gasoil and gasoline storage tank farm. The code followed is NFPA 11 and the system in question are "the Low-level foam discharge outlets for diked areas".
The tank farm will consist of 6 gasoil tanks and 6 gasoline tanks. See image below for simple sketch of arrangement.
Secondary spill containment will consist of external bund wall of 1.8m high (Black Line in Image), with 0.5m tall intermediate bund walls separating each tank (Red Line in Image).
When applying the application rate of 4.1 L/min/m2 for AFFF (NFPA 11, Table 5.7.3.2), we are debating whether to apply the foam to the smaller intermediate net bunded area per tank (E.g. Bund Area A), or do we apply it to the overall full tank farm net bund area for all 6 tanks (Bund Area A+B+C+D+E+F)?
Of course the water requirements for the smaller intermediate bund area is considerably more cost effective.
Further info:
Each tank will be fitted with fixed top foam pourers and shell cooling sprinkler systems, supplemented by foam and fire water hose streams.