I have been trying to interpret the revised 2010 NFPA 11 Section 4.7 - Piping for a while. My conversations with various AHJs have been conflicting to say the least.
Question:
Does piping outside of the hazard area need to be galvanized?
I can justify other materials/finishes are suitable based on the following:
4.7.1.3 - Pipe outside of the hazard area shall conform to the materials allowed by NFPA 24.
4.7.2.5(2) - Other C-values for corrosion resistant piping materials IAW NFPA 13.
So I believe it still provides an option to use other than galvanized pipe, but it is not straightforward. Looking at the previous issue and the report on proposals excerpts, it appears the Standard's committee fought back hard to make it a galvanized only standard. So why leave any room for interpretation/exceptions? If HDPE or cement lined pipe is acceptable outside the hazard area, why doesn't 4.7.2.5(2) reference NFPA 24 since HDPE and cement lined pipe are not included in NFPA 13?
For background - Our applications are typically flammable liquids storage tank protection, so we end up with both buried and above ground foam header piping >10" diameter, downstream of the proportioner, extending thousands of feet around tank farms. HDPE and painted, cement Lined CS are ideal materials for use outside of the hazard area for buried and above ground headers, respectively. To use anything else is hard to justify.
Thanks in advance for your replies.
JP
I have been trying to interpret the revised 2010 NFPA 11 Section 4.7 - Piping for a while. My conversations with various AHJs have been conflicting to say the least.
Question:
Does piping outside of the hazard area need to be galvanized?
I can justify other materials/finishes are suitable based on the following:
4.7.1.3 - Pipe outside of the hazard area shall conform to the materials allowed by NFPA 24.
4.7.2.5(2) - Other C-values for corrosion resistant piping materials IAW NFPA 13.
So I believe it still provides an option to use other than galvanized pipe, but it is not straightforward. Looking at the previous issue and the report on proposals excerpts, it appears the Standard's committee fought back hard to make it a galvanized only standard. So why leave any room for interpretation/exceptions? If HDPE or cement lined pipe is acceptable outside the hazard area, why doesn't 4.7.2.5(2) reference NFPA 24 since HDPE and cement lined pipe are not included in NFPA 13?
For background - Our applications are typically flammable liquids storage tank protection, so we end up with both buried and above ground foam header piping >10" diameter, downstream of the proportioner, extending thousands of feet around tank farms. HDPE and painted, cement Lined CS are ideal materials for use outside of the hazard area for buried and above ground headers, respectively. To use anything else is hard to justify.
Thanks in advance for your replies.
JP